Re: 3ph motor starting
I'm not sure I understand your question.
Are you are referring to the operation of a Wye-Delta Starter (sketch below shows the power circuit only, the control circuit is not shown).
To use a motor with a wye-delta starter, it must have enough leads brought out so that the connection can be changed from wye to delta.
Also, the motor must be "delta-wound", that is, designed to operate with the three windings delta connected.
It is started (for a few seconds), with the windings wye connected. Each phase gets only 58% of rated voltage, and starting current (and torque) are lowered. The starter then re-connects the windings in delta for running.
This feature can be used to reduce the inrush current during starting.
If you are asking about the starting characteristics of a wye-wound motor versus a delta-wound motor, the starting characteristics of a motor are not determined by whether the motor stator is wye-wound or delta wound.
Induction motor starting characteristics are determined mostly by the rotor resistance.
Ed