Your fla are good on primary and secondary. Are you basing your breaker sizes from the NEC ?I'm trying to make a simple quick reference chart. Does someone mind confirming my math? See attached picture
My math is basically as follows... if you have a breaker on both side then pri. is 250% of FLA but have to round breaker down, sec. breaker is 125% rounded up to next size. If breaker only on primary then its 125% rounded up to next size. I'm pretty sure that's how its done, hence the need for me to get it checked by other eyes haha. i do understand that some don't seem "typical" but this is more of a chart for what's allowed by the NEC, you can always resort back to more typical but this is a "not to exceed" type of thing.
1. Every thing 800A and below you can round up to next standard size, you will need to round down everything above 800A.I'm trying to make a simple quick reference chart. Does someone mind confirming my math? See attached picture