3Ph ungrounded delta system 230 volts
just about anything is possible, or so i have been told.
normally it will be close to the same from each phase, about 130 Volts.
but I have seen it 20 or 30 volts different from one phase to another.
Anywhere from 0V (which is most unlikely) upto 460V (and higher during a fault condition). It is all dependent on the system loading, coupling capacitance, and the input impedance of your meter. In reality, I would be most surprised to find a reading of 138V.
No way!
No way!
infinity said:
If the system is ungrounded shouldn't the voltage to ground be zero?
If the line to ground voltages were all zero, the line to line voltages would be zero as well. Not good.
Imagine equal stray capacitances between each line and ground. This would form a wye network, and Vline-ground would be Vline-line/1.732.
Of course this network would be easily unbalanced. Then we have a different problem.
I ran into an ungrounded system with imbalance currents (single phase 208 loads), the voltage to ground varied with the phase loads. I did not mess with this as much as I might today (this was 26 years ago). I just grounded the XO like it should have been.
How would you get 460 volts from a 230 volt system?
During a fault condition it is possible to approach 2x line-line voltage on ungrounded delta systems. It is not common and has to do with when and where the fault occurs.