Originally posted by molotov27: Anyone can shed any light on which is the correct way to go with this??
I?ll give it a try.
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Using the calculator from the Mike Holt Home Page ?Free Stuff,? I get a result of 3.128 volts. That equates to a 1.5% voltage drop in a 208 volt system. The spreadsheet uses the formula VD = 1.732 x K x L x I / CM</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Using the formula that is described in the NEC Handbook, Article 215.2(A)(4), I get the same result of 3.128 volts. The Handbook uses the formula VD = 2 x L x R x I x 0.866 / 1000</font>
<font size="2" face="Verdana, Helvetica, sans-serif">
If you try both methods, the one suggested by bphgravity, which I have seen in other references and this one, you get different answers.
What I did differently is that I used the DC Resistance value from Table 8 (i.e., 0.0258 ohms/1000 feet), instead of the ?AC Effective Impedance at 0.85% power factor? value from Table 9 (i.e., 0.043 ohms/1000 feet).
Please note that the explanation in the cited Handbook article explicitly states that it is using the Table 8 information. Note also that the explanation following Table 9 in Handbook says,
Voltage drop calculations using the dc-resistance formula are not always accurate for ac circuits, especially for those with a less-than-unity power factor or those that use conductors larger than 2 AWG.
The reason that ?larger than 2 AWG? comes onto the picture is that the ?self-inductance? of a conductor is closely related to its cross-sectional area. For smaller conductors, the inductance is so small that it can be neglected.
Finally, note that there is no code requirement limiting voltage drop to a maximum value. It is a design issue. My first suggestion is to use the 2 x K x L x I / CM (or for three phase, 1.732 x K x L x I / CM), or use the Mike Holt Free Calculator (which uses this same formula). My second suggestion is that you accept the result, and look no further into the issue, if one of the following are true:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Your result is well below the 3% / 5% values suggested by the NEC.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Your conductor run is shorter than 100 feet.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Your conductor size is smaller than # 2.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">If you don?t meet any of these three, then you might take the next step of using the other formula (2 x L x R x I / 1000, with this formula multiplied by 0.866 for three phase), and that you use the Effective Z value from Table 9.