I have six POTs (transformers) that are aerial distribution mounted on a ground pad in a small enclosed fence. This trasformer yard has two sets of 208/120volt, 3 phase, wye-wye connected transformers servicing two separate buildings with a 12,460volt primary incomming from the substation. This is a NEC code violation since these live parts should be mounted on a pole high above the head. I am therefore going underground with the service drops from the two 3 phase transformers and installing a new pad mounted transformer to service both buildings (size to be determined later). Three of the POTS service one building and 3 of the POTS service another building. Each POT is 100KVA, so 6 of them add up to two sets of 300KVA, three phase, 208/120Volt wye-wye connected transformers per building.
A load study was performed by a consulting firm. This yielded 33amps on the secondary feed for the service drop on one building and 20 amps for the other building. This is demand load amps I am assuming.
I calculate 278 amps capacity for the secondary for both transformers: 100,000VA/(1.73*208Volts)=278 amps.
One of these buildings is a large manufacturing facility. I certainly can not image only 33amps of demand load from this type of a building after all single phase and 3 phase loads are added together. The other building is a fairly large office with much equipment. I can not imagine only 20 amps of demand load for that building.
I know all the loads emanate from the 3 phase main distribuition panel (typically sized for a 400 amp demand load) in parallel paths so that the demand current draws for each loaded circuit add in parallel. It is common to feed 3 phase loads directly from the 3 phase main distribution panel and feed 125amp single phase panelboards from the 3 phase main distribution panel.
Is there something I am missing here? A 33 amp load draw from a large manufacturing building as determined by the consulting firm in their load study??
A load study was performed by a consulting firm. This yielded 33amps on the secondary feed for the service drop on one building and 20 amps for the other building. This is demand load amps I am assuming.
I calculate 278 amps capacity for the secondary for both transformers: 100,000VA/(1.73*208Volts)=278 amps.
One of these buildings is a large manufacturing facility. I certainly can not image only 33amps of demand load from this type of a building after all single phase and 3 phase loads are added together. The other building is a fairly large office with much equipment. I can not imagine only 20 amps of demand load for that building.
I know all the loads emanate from the 3 phase main distribuition panel (typically sized for a 400 amp demand load) in parallel paths so that the demand current draws for each loaded circuit add in parallel. It is common to feed 3 phase loads directly from the 3 phase main distribution panel and feed 125amp single phase panelboards from the 3 phase main distribution panel.
Is there something I am missing here? A 33 amp load draw from a large manufacturing building as determined by the consulting firm in their load study??