3phase circuit for single phase load

Status
Not open for further replies.

Ravenvalor

Senior Member
Location
Triad region of NC
Occupation
Electrician
Hello and thanks for all of the indispensable advice.
Can I add a 208v 20amp receptacle to a 208v 20amp 3phase circuit if both loads combined only pull 10amps and both loads are right next to each other?
thanks so much for the help...
 
Might even be able to place the two loads 1000 feet apart and still no problem - until you give us some detail that sends us to some code section that says otherwise.;)
 