3phase induction motor, P1 and P2 terminals for external control circuit

Status
Not open for further replies.

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
If one is not going to use the thermostat built in the motor to control (shut off there starter) , can P1 and P2 wires be capped off separately in the terminal box? I see no reason why the two would need to be tied together, as from the nameplate it looks like a NC set of contacts.
 
You only need one cap if you cap them together....sometimes space is limited in the motor junction box.
 
Yes, and the unavoidable, “but” I have seen motors if the t stat leads are not connected it voids the warranty. I would consider the cost, time, to replace the motor.
 
Yes, and the unavoidable, but I have seen motors if the t stat leads are not connected it voids the warranty. I would consider the cost, time, to replace the motor.
Luckily this is a bid-engineered job so will go back on the company we are working for, just on this job a couple days helping out on some intake fans. I’m sure they have some other source of overload protection figured already.
Honestly my first time seeing this on a 3ph induction motor though I’m sure it’s fairly common thing.
 