3pole 20amp gfci circuit

Status
Not open for further replies.

Cubp

Member
Location
Texas
Occupation
Electrician
I have a customer that wants to add a 3 phase 20 amp circuit. Where he needs it is near a sink. I can't find a 3pole 20amp gfci breaker that works with the panel. Any suggestions.
 
Small sub-panel that will hold a GFCI?

(what panel do you have in already?)

It's a seimens QP. I don't like the situation but being that it's 3 phase 230v does it need to be gfci protected? It's a cord plug connected peice of equipment.
 
Doesn't someone make a dead-front GFCI device with an external donut for passing your own circuit wires through?
 
Specifically 210.8(B) only mandates GFCI for single phase:

(B) Other Than Dwelling Units.
All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts or less to ground, 100 amperes or less, installed in the locations specified in 210.8(B)(1) through (B)(12) shall have ground-fault circuit-interrupter protection for personnel.
 
Specifically 210.8(B) only mandates GFCI for single phase:

B) Other Than Dwelling Units.
All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts or less to ground, 100 amperes or less, installed in the locations specified in 210.8(B)(1) through (B)(12) shall have ground-fault circuit-interrupter protection for personnel.

😗
 
Doesn't someone make a dead-front GFCI device with an external donut for passing your own circuit wires through?

Leviton makes one that is designed for use with a shunt trip breaker or I believe certain contactors. Its not listed only recognized.
 
Specifically 210.8(B) only mandates GFCI for single phase:
(B) Other Than Dwelling Units.
All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts or less to ground, 100 amperes or less, installed in the locations specified in 210.8(B)(1) through (B)(12) shall have ground-fault circuit-interrupter protection for personnel.


B) Other Than Dwelling Units.
All 125-volt through 250-volt receptacles supplied by single-phase branch circuits rated 150 volts or less to ground, 50 amperes or less, and all receptacles supplied by three-phase branch circuits rated 150 volts or less to ground, 100 amperes or less, installed in the locations specified in 210.8(B)(1) through (B)(12) shall have ground-fault circuit-interrupter protection for personnel.

Ok. So what Code is the OP on?? And keep in mind that things required by the 2020 haven't been invented yet.

-Hal
 
While I posted the quote from the 2020 code, the single-phase restriction has been there for a long time...
Here's the text that appears in the 2011, 2014, and 2017 codes:
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(B)(1) through (8) shall have ground-fault circuit-interrupter protection for personnel.
 
While I posted the quote from the 2020 code, the single-phase restriction has been there for a long time...
Here's the text that appears in the 2011, 2014, and 2017 codes:
All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in 210.8(B)(1) through (8) shall have ground-fault circuit-interrupter protection for personnel.
That is for Dwelling Units... I'm guessing if this is 3-phase, it is not residential... in which case NEC 2017 states... 1604605700748.png
 