Re: 3rd floor conduit
Under the 2002 and earlier rules romex was allowed in a 4 story building IF the first floor is used strictly for parking.
However, the reference to building construction types now allows up to 5 stories IF the building has a sprinkler system and the contruction method has a 1 hour fire rating.
However, if your building code is BOCA, UBC or whatever you then face the task that building construction is named and rated differently.
Also, some states ( Ohio, Pa., Mass. )allowed romex in more than 3 story buildings if the circuit stayed on 1 floor and the building had a sprinkler system. There was even a version of romex that was rated for use in plenum ceilings.
However, 334.10 seems to require that romex in barns be concealed behind type X drywall!!!! This seems to be an oversight because barns and factories are still allowed to be wired with open wiring on insulators provided that the wiring does not need to be articles 501 or 502 rated.