Aside from input voltage imbalance, what can cause 3rd harmonic on a typical 6 pulse, non-active front end VFD? I have checked the source and it is balanced. There is also a passive harmonic filter upstream to VFD which I think creating - or at least amplifying - 3rd harmonics. There is about 3% 3rd harmonic which is pretty high considering that 5th and 7th are about 3%. The passive harmonic filter is a line reactor (upstream and in series with VFD), trap reactor and trap capacitors (both upstream and in parallel with VFD). When I take the trap circuit off-line 3rd harmonics drop to almost 0 but needless to say TDDi goes up to about 20% as expected.
Our client requires us to meet IEEE519 by having TDDi<5% (ISC/IL=20) so it is already hard to meet the specs without the stupid 3rd popping up out of nowhere. Harmonic filter manufacturer says something about VFD PWM frequency "drifting" and thus causing the 3rd but I am not buying it. I even measured the voltage drop across trap reactor and there was about 10% difference between a phase and other 2.
Our client requires us to meet IEEE519 by having TDDi<5% (ISC/IL=20) so it is already hard to meet the specs without the stupid 3rd popping up out of nowhere. Harmonic filter manufacturer says something about VFD PWM frequency "drifting" and thus causing the 3rd but I am not buying it. I even measured the voltage drop across trap reactor and there was about 10% difference between a phase and other 2.