A coworker installing equipment in China was getting shocked on a computer rack. The electricians checked the power circuit and insist that everything is right. I told him to check the ground connection in the outlet box that the UPS from the rack plugs into. The box was not bonded to ground. He added a bonding jumper in the box and does not get shocked any more, but there is 3V between the ground and neutral wires. Should we be concerned about this?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
but there is 3V between the ground and neutral wires. Should we be concerned about this?
If this is wired like our systems here in the US, that voltage reading is the voltage drop on the neutal conductor.
Don
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
sgokie said:
A coworker installing equipment in China was getting shocked on a computer rack. The electricians checked the power circuit and insist that everything is right. I told him to check the ground connection in the outlet box that the UPS from the rack plugs into. The box was not bonded to ground. He added a bonding jumper in the box and does not get shocked any more, but there is 3V between the ground and neutral wires. Should we be concerned about this?

Are these Chinese electricians? having had some experience with Chinese electricians, I would take any utterance from themwith many grains of salt.
 

RayS

Senior Member
Location
Cincinnati
hmmm, 'round here you can't bond the ground and neutral except at the service- kinda hazardous if the neutral gets broken and lights up the equipment grounds
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Where is the 3-volts being observed? Is the source neutral bonded to ground?

If the 3-V is measured at the point of use, and the supply source neutral is bonded the same way we do here in the US, then you are just seeing the normal I*R drop (voltage) developed on the neutral from the source to the load.
 