Does anyone know why Table 310.15 (B) (17) lists the ampacity of 4/0 at 360 amps but wire spec sheets list at 480 amps? Also any idea what it would be at 90*C?
One table is for insulated the other is for bare.
310.15(B)(21)Does the code have a table for bare wire?
You can only compare ampacities where all of the conditions are the same. The first bare ampacity table you posted is based on a 25°C ambient, and a maximum 75°C conductor temperature. The second on a 40°C ambient and 80°C conductor temperature. The first is based on a 50°C rise and the second on a 40°C rise.Thanks... but still confused as to why the ampacities are different.
You can only compare ampacities where all of the conditions are the same. The first bare ampacity table you posted is based on a 25°C ambient, and a maximum 75°C conductor temperature. The second on a 40°C ambient and 80°C conductor temperature. The first is based on a 50°C rise and the second on a 40°C rise.
4/0 @ 75C is 360, @90 C it's 405C , Bare is 480
Release of heat I guess. Insulated =lower rating, covered middle rating, bare higher rating
Bare conductors can cool much faster than insulated conductors. Remember that the word "insulation" is used for both resistance to electrons passing through and resistance to heat passing through.
Current-Temperature of Bare Overhead Conductors for no sun, wind 2ft/s and ε[Emissivity (0.23 to 0.91)]=0.23 the ampacity of 4/0 copper [75oC conductor 25oC air]=487 A