Is there a code requirement to have to provide protection for a 4/0 SER cable that is fastened to the bottom side of floor joists in an unfinished basement?
338.10(B)(4)(a) sends you to 334.15(C) which states its ok to support SE cable to the lower edges of the joist as long as the cables are not smaller than two 6 awg or three 8 awg