I was recently turned down on a service inspection at a commercial building.
I set a 200 amp feed through panel adjacent to the meter base and fed through the structure basement with 4/0 XHHW Al conductors in PVC conduit to a 200 amp panel.
4/0 feeders were landed on the feed through lugs protected by the 200 amp main.
Inspection tag states that the installed conductors do not meet the ampacity rating of the OPD.
Chart lists this wire at 180 A 75 deg.
Next size breaker up is 200A
The total load computed is just over 100 amp.
Am I wrong??