4.16kV feeder cable, each phase in separate conduit

Status
Not open for further replies.

Designer69

Senior Member
We have a situation where we are installing 3-1c 750MCM cables to a disc. sw. and the current design is to route each phase cable in a separate conduit.

An engineer raised a concern that this configuration would create eddy/circulating currents and it's better to use 1 conduit for all 3 phases or a tray.

I haven't heard this before so I was wondering what your thoughts are and if it's a valid concern.

Thank you
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
We have a situation where we are installing 3-1c 750MCM cables to a disc. sw. and the current design is to route each phase cable in a separate conduit.

An engineer raised a concern that this configuration would create eddy/circulating currents and it's better to use 1 conduit for all 3 phases or a tray.

I haven't heard this before so I was wondering what your thoughts are and if it's a valid concern.

Thank you

NEC 300.35 addresses this type of installation.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
170831-1438 EDT

To minimize external magnetic fields you always want to run the supply and return path conductors as close as possible to one another so as to cancel their magnetic fields.

Changing magnetic fields about a conductor induce a voltage in the conductor.

If you have a single long straight wire with current flowing thru it and the return path for that current is a long way away, then the magnetic field around that wire will drop off as the inverse of the radial distance from the wire for radial distances small compared to the distance to the return current path.

Put a conductor, a hunk of metal, in that field and make the field oscillate (AC current), then that metal will heat from induced voltage and current.

.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
At first, you may use one single-core cable per duct if the reinforcing bar[rebar] are only outside the group of ducts-in the envelope of the duct bank.
The ampacity will rise but the reactance between phases will rise also and so the voltage drop will rise. For short length it is o.k.
 