I'm looking at an application with a new 4.16kV MCC where the customer wishes to serve L-N loads. I've never been involved with a MV MCC that required a neutral as most of the 4.16kV systems have either been LRG systems or just 3-Wire systems.
Based on the requirements of 250.30 I'm trying to determine if we need to have a neutral bus in the MV MCC and bring the neutral to this bus with bonding to ground or if we can just bring the neutral directly from the transformer to the load since only one load requires this neutral. I've always had situations with LV switchgear where the neutral was brought into the first disconnecting means with the system bonding jumper being either at the transformer or the first disconnecting means.
If the system bonding jumper is provided at the transformer secondary is there a requirement to bring the neutral into the first disconnecting means as opposed to routing it directly to the load or another location outside of the switchgear? The only potential functional issue that I'd see would be with ground fault settings with the CT's/relay not seeing the neutral current but am not sure from an NEC standpoint if this would be compliant.
Based on the requirements of 250.30 I'm trying to determine if we need to have a neutral bus in the MV MCC and bring the neutral to this bus with bonding to ground or if we can just bring the neutral directly from the transformer to the load since only one load requires this neutral. I've always had situations with LV switchgear where the neutral was brought into the first disconnecting means with the system bonding jumper being either at the transformer or the first disconnecting means.
If the system bonding jumper is provided at the transformer secondary is there a requirement to bring the neutral into the first disconnecting means as opposed to routing it directly to the load or another location outside of the switchgear? The only potential functional issue that I'd see would be with ground fault settings with the CT's/relay not seeing the neutral current but am not sure from an NEC standpoint if this would be compliant.