I am an electrical designer working on a change of plan for a project I didn't design. The project is for a bridge. 2000 feet of underground conduit has 4#4/0 & 1#1/0 Ground then continues to 2 conduits within a bridge parapet - one is spare and the other is 4#4/0 & #1/0 ground to feed roadway lighting. The circuit is protected by a 70A circuit breaker.
My 2 questions are:
Why did the original designer indicate for #1/0 ground? I think there is a restriction to Table 250.122 that I wasn't able to find. (Perhaps, it was due to 4 conductors being installed within a conduit or due to possible future use of the spare conduit).
During my change of plan, the load was reduced and voltage drop decreased. The 2000 feet of 4#4/0 & #1/0Ground is already constructed. Only the wiring within the parapet is being reduced to 4#2/0. I don't know what to do with the ground wire. Can the ground wire be reduced and per what section of the code?
My 2 questions are:
Why did the original designer indicate for #1/0 ground? I think there is a restriction to Table 250.122 that I wasn't able to find. (Perhaps, it was due to 4 conductors being installed within a conduit or due to possible future use of the spare conduit).
During my change of plan, the load was reduced and voltage drop decreased. The 2000 feet of 4#4/0 & #1/0Ground is already constructed. Only the wiring within the parapet is being reduced to 4#2/0. I don't know what to do with the ground wire. Can the ground wire be reduced and per what section of the code?