4/3 NM cable as dwelling feed

nizak

Senior Member
Existing single family dwelling built in the mid 80’s.

Load center is being fed with 4/3 NM cable from an exterior disconnect protected by a 100 amp breaker.

Am I correct in saying that wasn’t even compliant when it was new?

I’m looking to upgrade the service . Will have an 8 space 3R 200 amp main breaker panel adjacent to the meter.

Will that now need to be reduced to a 70 amp breaker because the NM rating for the 4/3 is 60 degree and it’s not feeding the entire dwelling?

I will be adding an EV charger and taking that load from the new panel outside.

Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Load center is being fed with 4/3 NM cable from an exterior disconnect protected by a 100 amp breaker.

Am I correct in saying that wasn’t even compliant when it was new?
If it were SER then #4 could be used if it carries the entire load. NM cable no good.
 