The individual conductors be bent in a tight 90° bend to enter the LB. If you were using a cable then the cable Article would tell you about the bend radius. For example SE cable can only be bent at a radius equal to a minimum ratio of 5X it's diameter. Making a tight 90° bend in that cable would be a violation if it didn't have a bend radius greater than or equal to 5X the diameter.Sorry I am having such a hard time with this. Thanks for sticking it out. 314.28 (A)(2) is titled "Angle or Upulls, or Splices." How can this not be about bending radii?