4 awg SO cord hook up to 150 amp three phase 480V. breaker

Status
Not open for further replies.

zappy

Senior Member
Location
CA.
So we're temporarily hooking up a dedicated piece of equipment that pulls 60 A. the cord is rated for 60 A but we're hooking it up to 150 amp breaker, that doesn't sound right but my boss says go ahead and do it. What does the code say about this? Thank you for your help.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
240.4 says that conductors shall be protected at their ampacity, but there are exceptions. Motors, air conditioners, welders are common ones, also tap conductors. If there is some kind of protection on the machine I might not be too worried about it.
 

jap

Senior Member
Occupation
Electrician
So we're temporarily hooking up a dedicated piece of equipment that pulls 60 A. the cord is rated for 60 A but we're hooking it up to 150 amp breaker, that doesn't sound right but my boss says go ahead and do it. What does the code say about this? Thank you for your help.

If the code could talk it would say ,,,, "Use me to settle any doubts you may have".

JAP>
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
So we're temporarily hooking up a dedicated piece of equipment that pulls 60 A. the cord is rated for 60 A but we're hooking it up to 150 amp breaker, that doesn't sound right but my boss says go ahead and do it. What does the code say about this? Thank you for your help.
It is unlikely the lugs on the breaker are rated for the fine stranding of a cord's conductor.
 