#4 for feeder and 3/4 offset

Status
Not open for further replies.

sfav8r

Senior Member
Just failed an inspection for 2 reasons and I'm curious what others think about this. The 2 reasons were that my guys used #4 for a house panel on a 9 unit building. The inspector said that the 100a feeder can only be #4 for residental DWELLING units and that the house panel serves hallways, a laundry room and a 2 car garage so it's not a dwelling unit. This seems lke a real stretch to me since any residential dwelling unit would have the same thing. The 2nd failure was for using a 1" 3/4 offset in a conduit run. They used the fitting to offset the conduit enough to get above a lip before penetrating a wall. The inspector said the offset fittings were not approved for that use, only to connect to a box. I've never heard that.

Any thoughts?
 
Did the inspector provide any code or UL references?
Install a lower rated OCPD assuming it will be within your calculated load and use the #4.
ASFAIK, The offset nipple is for rigid conduit to be used with an enclosure.
I will check my UL book to see if I can find anything on it.
 
The permission to use 4 AWG w/ 100A overcurrent protection only applies when it supplies the entire load of a dwelling, IMHO the inspector made the right call, if the load allows use a 90A breaker, or replace it.
 
I also agree.
As far as the offset nipple, I believe the killer is UL QCRV which states that fitting so that type "have only been investigated for use with locknuts."
 