316.15(B)(4)(c)On a 4-wire, 3-phase wye circuit where the major portion of the load consists of nonlinear loads, harmonic currents are present in the neutral conductor; the neutral shall therefore be considered a current-carrying conductor.
Gmack said:.
Wouldnt fly in my zip code.
iwire said:What woudn't fly?
infinity said:My 2 cents says that anything above 50% is a major portion. If you look at the Congress of the USA the majority leader is from a party with more than 50%. The minority leader would be from the party with less than 50%.
iwire said:What woudn't fly?
If the buildings load is 45% non-linear and 55% linear it has to fly.
Gmack said:You cant treat a "building" without regards to future expansion
Gmack said:Bob, Im my zip, the "big fish" have all read the writing on the wall with regards
to the "harmonic" issue. So has the NEC. AND so I have.
You cant treat a "building" without regards to future expansion
In my zip the GC/Neutral is the big issue. No one cares about allowing a minimum. Thats backward thinking.
I'm not familiar with this suggestion or the mandating the increase in size of the neutral by the NEC and EE's. Where could I find more information?NEC and all AIA's EE's are suggesting/mandating "up sizing" in advance.
I have talked with a number of engineers who design office buildings and they don't do anything special for the nonlinear loads and their buildings never have any problems. Also I find it very interesting that almost all of the information on this "problem" is authored by someone who works for a manufacturer that has an economic interest in correcting the "problem".Bob, Im my zip, the "big fish" have all read the writing on the wall with regards to the "harmonic" issue. So has the NEC. AND so I have.
RUWired said:O.K., So I'll start over with my question.I will be feeding three 400 amp main breaker panels from an outdoor service. Each of these panels have combinations of loads,Lighting-recpt.,hvac,computors on the network.Will the neutral in this case be a c.c.c.?
Rick