11Haze29
Member
- Location
- Rhode Island
- Occupation
- Electrical Engineer
Installation is a typical padmount xfrm (480/277) and an auxilary standby generator (480/277). Both have grounded neutrals and carry the neutrals to a Automatic Transfer switch. ATS manufacturer says install must be with a 4 pole ATS to switch the neutrals. He explained that without switching the neutrals, neutral current could split between the neutral conductor of the source, and through the ground path of the neutral conductor of the idled alternate source. I understand the logic. But where in the code does it say that the neutral must be switched to prevent the ground path from conducting current. Need a specific reference to convince the customer to justify added expense of the ATS. Any references?