Hopefully this is a simple question. I have a 4-pole ATS and wondering if it is possible to bypass the neutral in the ATS and solidly pass the neutral outside of the ATS, effectively turning this into a 3-pole switching system.
The issue is that we have a non-separately derived generator, but the ATS that arrived on site is 4-pole. I'm mainly looking for any code references or anything to indicate whether this is possible or not. After a pass through the NEC and NFPA 110 I was unable to locate anything to indicate that this wouldn't be possible.
The issue is that we have a non-separately derived generator, but the ATS that arrived on site is 4-pole. I'm mainly looking for any code references or anything to indicate whether this is possible or not. After a pass through the NEC and NFPA 110 I was unable to locate anything to indicate that this wouldn't be possible.