Has anyone ever had to install '4 pole' handle ties for anything?? Basically, tieing 2 , double pole breakers together.
Not me. I am curious. Why do you need or want to?
There have been pictures posted on this very forum of a four tied breaker, so they absolutely exist.
I do not believe there are any listed handle ties for four single pole units.
You may be able to find some factory four pole breakers with a single handle.
Keep in mind that a 4P breaker would be probably common trip and adding a tie handle wouldn't.
Do you mean "isolated ground"? I don't have a code book handy, but I would not have guessed that a hospital would have an ungrounded system.. . . were supplied by 2, branch circuits from an ISOLATION (Ungrounded) panel.
What manner of continuation of the practice would lead to the need to turn off four circuits at the same time? If a duplex has two power sources, then their breakers have to be able to be turned off at the same time. But even if you had a pair of duplexes in a 4x4 box being served by four separate sources, I don't think the code would require that all four be turned off at the same time.And if contractors etc. decide to continue this practice . . . , then they will need a '4 pole' handle tie.
If it's a QO panel, seems to me their handle ties can go on forever, IIRC.
Show me.![]()
Neener neener, I am sitting on my couch on my day off in my peejays.Can't right now, I am trying to get a bid together that covers 36 locations across six states.
Well, no, but from a practical standpoint I would expect much derision from the attempt.From a practical standpoint if you made one 21 poles long do you really think that turning off number 1 would turn off 41? Or even number 13?
Many 3-pole shunt-trip breakers have four-pole-sized handle ties.
Not that I'm aware of. But, if the OP is highly motivated . . .But can you buy those handles for field installation?
For some operating rooms, there are some 'ungrounded systems' NEC 2008 517.160 Isolated Power systems also 517.20 Wet procedure locations where the receptacles either have to be gfci protected IF the loss of power can be tolerated, if not tolerated then an iso system is required. Of course the iso (ungrounded system) is monitored 517.160(B)There are a couple aspects of this that I do not understand.Do you mean "isolated ground"? I don't have a code book handy, but I would not have guessed that a hospital would have an ungrounded system.
I think this is where the communication is lost.What manner of continuation of the practice would lead to the need to turn off four circuits at the same time? If a duplex has two power sources, then their breakers have to be able to be turned off at the same time. But even if you had a pair of duplexes in a 4x4 box being served by four separate sources, I don't think the code would require that all four be turned off at the same time. .
But, if the OP is highly motivated . . .