If my system utility voltage is 208Y/120V, and I have an emergency standby generator 480Y/277V. Do my ATS's needs to be 4-pole?
The way I understand in choosing between 3-pole and 4-pole ATS's depends on how I want my system to be grounded and how I want my OCPD's to react during a ground fault scenario in both utility and emergency side.
Additional information is that I have multiple separately derived system (transformer) in the building, the secondary side neutral of all this transformers will be connected to a common grounding electrode conductor which is connected to my main grounding electrode (in this case, a metal underground water pipe) with an additional supplementary ground as per code requirements. Note that this main grounding electrode is the one I am utilizing for my utility source.
Back to my question, do I need to have a 4-pole ats? or a 3-pole will be perfectly fine.
Please note: I don't intend to trip my generator breakers if I have ground fault when my system is being fed from the emergency standby generator.
Thanks in advance for those who will share their thoughts and knowledge.
The way I understand in choosing between 3-pole and 4-pole ATS's depends on how I want my system to be grounded and how I want my OCPD's to react during a ground fault scenario in both utility and emergency side.
Additional information is that I have multiple separately derived system (transformer) in the building, the secondary side neutral of all this transformers will be connected to a common grounding electrode conductor which is connected to my main grounding electrode (in this case, a metal underground water pipe) with an additional supplementary ground as per code requirements. Note that this main grounding electrode is the one I am utilizing for my utility source.
Back to my question, do I need to have a 4-pole ats? or a 3-pole will be perfectly fine.
Please note: I don't intend to trip my generator breakers if I have ground fault when my system is being fed from the emergency standby generator.
Thanks in advance for those who will share their thoughts and knowledge.