STRUT12034
If a 4" square box, used only for splices is supported within 18" of the box by 2 or 3 conduits, is a seperate hangar needed, thanks strutt12034
Man Chris,,,you're fast
So what you are saying is it would have to have threaded hubs?If a 4" square box, used only for splices is supported within 18" of the box by 2 or 3 conduits, is a seperate hangar needed, thanks strutt12034
The box would have to have threaded hubs?
OK, I have a 4" Square box facing the ceiling floating 18" above the floor, a 1/2" EMT enters from the right another 1/2" EMT leaves on the left. My conductors will be pulled through these raceways.
Now I need to support the box so I happen to grab some more EMT a single connector and make a support out of the back of the box to the floor. No conductors will be in this support.
Red tag or not?
Red tag or not?
Red tag or not?
Red tag it still doesn't comply with section 314.23 (E) and I don't think that you will find an emt connector that is listed to support anything. Use a piece of unistrut.
Since when do box supports have to be listed?
Is a screw listed?
And I am not using a raceway to support the box I am using round shiny tubing.
Is a screw listed?