in Table 31012(a) it shows that #4 copper thhn could be used for a single phase dwelling service & feeder. For a detached residential garage you can run #4 thhn for a 100amp subpanel?
This is a service with it's own meter?in Table 31012(a) it shows that #4 copper thhn could be used for a single phase dwelling service & feeder. For a detached residential garage you can run #4 thhn for a 100amp subpanel?
#2 AL would be good for 90AYou can do #4 cu on a 90a breaker and it's a cheap sweet spot or go to #2 AL. Just need a small enough calculated load of 85a.