4" trench 24" deep

Status
Not open for further replies.

EEC

Senior Member
Location
Maryland
In this size trench can we place a 2-1/2" PVC sch 40 and a 1" PVC sch 40 on bottom and cover with 18" of dirt?
 
The code does not concern itself with the trench dimensions, only the minimum cover requirements. The minimum cover depends on a number of factors, such as raceway type and the use of the ground over the pipe. This is explained in Table 300.5
 
EEC said:
Iam concerned whether the conduit can touch each other
Then worry not. This might violate a BICSI spec if the 1" is for the phone and cable, but those specs certainly don't have the force of law.
 
If that trench is only 24" deep and you need 24" of cover, you need to dig a little deeper (3" plus). The cover is measured from the top of the conduit, not the bottom of the trench.
steve
 