I am trying to find 4 wire cord rated for at least 125 amps and the SOOW cord in the NEC lists it at 85 amps, can someone point me in the right direction?
I suppose I could use the individual SC Cables and but since they can't come in contact with each other (Table 400.5A(2) Note 1 temperature rating of cable (167 deg. F) Column D note 1.
an ampacity not less than 125 percent of the full-load current rating of all resistance heating loads plus 125 per-cent of the full-load current rating of the highest rated motor plus the sum of the full-load current ratings of all other connected motors and apparatus based on their duty cycle that may be in operation at the same time.
I am trying to find 4 wire cord rated for at least 125 amps and the SOOW cord in the NEC lists it at 85 amps, can someone point me in the right direction?