Can a 4-wire A.T.S. with a solid neutral,be used on a 3-wire system with out any metering currents showing up on the ground wire?
The neutral from the utility is bonded in the main ocpd and goes no further. The neutral is bonded in the gen set ocpd's ( 2 ea.) and goes no further.Ground wires interconnect every thing all the way into the building.
Might also ask, does the ground fault protection in the main gear work off the current on the ground wire or the difference between the the current on the neutral and the ground wire?
The neutral from the utility is bonded in the main ocpd and goes no further. The neutral is bonded in the gen set ocpd's ( 2 ea.) and goes no further.Ground wires interconnect every thing all the way into the building.
Might also ask, does the ground fault protection in the main gear work off the current on the ground wire or the difference between the the current on the neutral and the ground wire?