4 wire cable question

Status
Not open for further replies.

hoov

New member
I was looking at a 4 wire 100 amp aluminum sub feed cable
> 2/2/2/4 and my question is for a 100 amp feeder (100 amp sub panel in
> another building (Garage) The NEC requirements for the grounding or bonding wire are
> to be a #6, since #2 covers the requirements for the grounded and ungrounded
> wires current wise why would the manufacturer go to a # 4 for the grounding
> or bonding wire, also is it OK for that wire (bonding) to have no insulation?
 

luke warmwater

Senior Member
Re: 4 wire cable question

When you say "another building (garage)", are you talking about a detached garage?? If so, how did you run this SER cable??
 

hornetd

Senior Member
Location
Maryland
Occupation
Journeyman Electrician, Retired
Re: 4 wire cable question

The designation SER is for "Service Entrance, Retardant" The cable is designed to serve as three phase service entrance cable and the bare conductor is sized to serve as the neutral.
--
Tom
 
Re: 4 wire cable question

hornetd : the ser cable you describe you can use it one way but mainly it was used for single phase service with separte netural and ground if you take the outer skin off and see the conducter marking there i know one will be black and red stripe and white or light grey ( one of two) and bare alumine conducter for grounding that one way i use it both way but for three phase i use the diffrent cable it will be ser cable but specal maded for 5 conducters for 3 hot conducters and neutral and grounded conducters that cost kinda expensive than the reguar cables are

merci marc
 