Fordean
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
Car charger are coming with a 4 wire l14-50 plug. 2 wire +G wiring diagram. Are we required to run a neutral. Even though it is not used.
That's not correct. A NEMA 10-30 is an ungrounded receptacle providing L1, L2, and neutral. The allowance in 250.140 Exception is to bond the frame of a dryer to the grounded conductor (neutral) in certain existing circumstances, as there is no EGC.I was on Reddit looking at the EV charging thread and someone had stated that 3 wire dryer plugs are “”L1, L2, and Neutral”
I responded with a correction that all 3 wire dryer plugs are L1, L2, and a ground, which is correct.
It is used for both purposes with the exception permitting the neutral to also serve as the equipment grounding conductor. The cable that feeds the receptacle will have a white conductor but will not have a green or bare conductor.If the frame of the dryer is bonded, doesn’t that make it a ground?
No. Look at enclosures on the utility side of the service disconnect--they are also bonded to the grounded conductor to provide a fault clearing path, as no EGC is present, since the EGC system is created at the service disconnect.If the frame of the dryer is bonded, doesn’t that make it a ground?
Very thorough. I like it! Thanks Wayne!No. Look at enclosures on the utility side of the service disconnect--they are also bonded to the grounded conductor to provide a fault clearing path, as no EGC is present, since the EGC system is created at the service disconnect.
An EGC is a conductive path at earth potential that does not carry current during normal operation and is used for bonding so that, at least on a grounded supply, any fault to non-current carrying metal parts will complete a fault current path to trip the breaker. A grounded conductor, on the other hand, is at earth potential at the service, but is used to carry current during normal operations.
Since a dryer generally has 120V loads, on a 3 wire receptacle the earth potential wire is a grounded conductor, not an EGC. By special allowance due to historical factors, we get to us the grounded conductor for bonding in some existing such installations.
If you get a dryer that is 240V only (some European models), then you could possibly convert the 10-30 receptacle to a 6-30 receptacle by repurposing and reidentifying the former grounded conductor as an EGC. NEMA 6-30 is L1, L2, and ground.
Cheers, Wayne