The white wire is a bonding connection to the frame of the dryer and is connected to the grounded conductor. This set up is okay if the existing Dryer receptacle is 3 wire. If you are installing a 4 wire Receptacle and plug.…you remove the white jumper that goes to the green screw. With the new four wire you attach the equipment grounding conductor to the green screw. I believe that in the 1986 code is when the three wire method was no longer allowed unless it is an existing installation. This is why dryers and ranges typically do not come with a cord attached to the appliance already!The existing dryer has a 3 wire set up. I am trying to wire it 4 wire, and I am not sure why this white factory wire is landed on the grounding terminal. What do I do with the existing white wire? Do I move it to the neutral termination point since I am bringing a 4 wire / ground wire?
It didn't get moved when the appliance guys delivered and hooked up my cousin's dryer, but I fixed itAnd typically the jumper does not get moved when the HO installs a 4 wire cord
Yes, and 90% of appliance installers will leave it connected to the frame on a 4-wire install!Correct. The white wire is there to bond the cabinet to the neutral in 3-wire installations.
It's stored on the neutral terminal in 4-wire installs to keep it from touching anything else.