jwjrw Senior Member Oct 29, 2010 #1 What is the article # requiring sub panel's to be fed with a 4 wire. I left my book at work.
acrwc10 Master Code Professional Location CA Occupation Building inspector Oct 29, 2010 #2 Pipe ? Romex ? SER ? SEU ? how are you getting there?
jwjrw Senior Member Oct 29, 2010 #3 acrwc10 said: Pipe ? Romex ? SER ? SEU ? how are you getting there? Click to expand... SER is the plan. Last edited: Oct 29, 2010
acrwc10 said: Pipe ? Romex ? SER ? SEU ? how are you getting there? Click to expand... SER is the plan.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Oct 29, 2010 #4 Basic rule goes back to 250.24(A)(5) Seperate building you are probably referencing 250.32(B) Last edited: Oct 29, 2010
jwjrw Senior Member Oct 29, 2010 #5 augie47 said: Basic rule goes back to 250.24(A)(5) Seperate building you are probably referencing 250.32(B) Click to expand... Yep that was the one. Thanks!
augie47 said: Basic rule goes back to 250.24(A)(5) Seperate building you are probably referencing 250.32(B) Click to expand... Yep that was the one. Thanks!