4 wire feeder

Status
Not open for further replies.

iaov

Senior Member
Location
Rhinelander WI
Don't have my book with me at the moment and need to know what is the Code Article that requires a 4 wire feed to a sub panel. Thanx all!
 
I don't know that there is a requirement of a 4 wire feeder to a sub-panel :D. I approve many sub-panels with a 3 wire feeder.
 
Single phase, Three wire with ground. If using a non-approved raceway for grounding the feeders would be required to be four conductors, two hots, grounded conductor, and a grounding conductor per 250.24(A)(5).
 
Single phase, Three wire with ground. If using a non-approved raceway for grounding the feeders would be required to be four conductors, two hots, grounded conductor, and a grounding conductor per 250.24(A)(5).

Single phase 120 volt panel would be a two wire with ground feeder. :wink:

Roger
 
agree.
Now, what if there is no neutral load (such as a 240 volt HVAC sub-panel--no neutral) ?
The OP didn't specify 3 phase 4 wire with ground, he just said sub-panel :smile:
 
This triggered a question for me. In the pre-'08-NEC world, could one run a 120v circuit to a separate building, and use only two wires, by re-grounding the grounded conductor?
 
This triggered a question for me. In the pre-'08-NEC world, could one run a 120v circuit to a separate building, and use only two wires, by re-grounding the grounded conductor?

if it met the other requirements of 250.32, yes.
 
agree.
Now, what if there is no neutral load (such as a 240 volt HVAC sub-panel--no neutral) ?
The OP didn't specify 3 phase 4 wire with ground, he just said sub-panel :smile:

True, but don't forget to installed the bonding screw to bond the cabinet. I see where some electricians will land the EGC on the insulated terninal block and forget they are required to install the bonding screw using this condition (no neutral loads).
 