Don't have my book with me at the moment and need to know what is the Code Article that requires a 4 wire feed to a sub panel. Thanx all!
Single phase, Three wire with ground. If using a non-approved raceway for grounding the feeders would be required to be four conductors, two hots, grounded conductor, and a grounding conductor per 250.24(A)(5).
This triggered a question for me. In the pre-'08-NEC world, could one run a 120v circuit to a separate building, and use only two wires, by re-grounding the grounded conductor?
agree.
Now, what if there is no neutral load (such as a 240 volt HVAC sub-panel--no neutral) ?
The OP didn't specify 3 phase 4 wire with ground, he just said sub-panel :smile: