4-wire panelboard
wmthompson90
ky
electrician
If a panel is stamped 3phase 4 wire am I required to pull a neutral if there will be no neutral loads? This will be a sub panel.
Does a 3 phase, 3 wire panelboard require the proper labeling to indicate that it doesn't have a neutral?
Yes but the panel in the OP is labeled 3 phase, 4 wire so it's not obvious that it does not contain a neutral conductor.
Yes, but your questions was for a 3 phase 3 wire panel. I don't think there is any requirement to mark a 3 phase 4 wire wire panel that is wired without a neutral, but it would be a good practice.
Seems a lack of a white, or gray, conductor on the grounded conductor bar might be a clue!
You're assuming that someone will actually remove the cover. It's more likely that someone will look at the panel label see 3Ø, 4W and assume that there is a neutral. I'm not aware of a particular code section that would require the proper label to be installed on the panel but figured I would ask.
Well they're going to have to open it to install their circuit. Surprise!, no neutral!
Been there, done that. Similar to finding dead fronts that have more breaker knockouts than actual breaker buss spots.......after you bid the job :)
I learned the hard way to open the panel before quoting. There are several brands that have more KO for breakers than spots on the bus. I think they just use the same cover for different size panels to save on mfg and inventory.
Another "gotcha" is some 100A panels where the main is in the branch circuit area on the bus, don't allow breakers opposite the main. There are KO's there but no place for the breaker.
Look at 2020 408.58.
I would think if installer does not maintain the voltage system marked by manufacturer he must apply a new label.
Cannot recall the number of times I have been burned by this....even on SERVICEs where no neutral was pulled in from the utility transformer.
One of these services was a building owned by the POCO.
Before electing to not pull the neutral keep in mind a lot of 240v loads now require GFCI protection and GFCI breakers need a neutral to work properly.