If a panel is stamped 3phase 4 wire am I required to pull a neutral if there will be no neutral loads? This will be a sub panel.
Longer answer: No, not required at all!short answer: No, not required
Nah, they will just land the neutral to their new thingy on the ground barReal short answer is that you or someone in the future will thank you if you do run a neutral.
-Hal
I am not aware of any requirement.Does a 3 phase, 3 wire panelboard require the proper labeling to indicate that it doesn't have a neutral?
Not as long as the source feeding it is grounded.Does a 3 phase, 3 wire panelboard require the proper labeling to indicate that it doesn't have a neutral?
Doesn't 3 phase, 3 wire, automatically tell you that?Does a 3 phase, 3 wire panelboard require the proper labeling to indicate that it doesn't have a neutral?
Yes but the panel in the OP is labeled 3 phase, 4 wire so it's not obvious that it does not contain a neutral conductor.Doesn't 3 phase, 3 wire, automatically tell you that?
Yes, but your questions was for a 3 phase 3 wire panel. I don't think there is any requirement to mark a 3 phase 4 wire wire panel that is wired without a neutral, but it would be a good practice.Yes but the panel in the OP is labeled 3 phase, 4 wire so it's not obvious that it does not contain a neutral conductor.
You're assuming that someone will actually remove the cover. It's more likely that someone will look at the panel label see 3Ø, 4W and assume that there is a neutral. I'm not aware of a particular code section that would require the proper label to be installed on the panel but figured I would ask.Seems a lack of a white, or gray, conductor on the grounded conductor bar might be a clue!
Well they're going to have to open it to install their circuit. Surprise!, no neutral!You're assuming that someone will actually remove the cover. It's more likely that someone will look at the panel label see 3Ø, 4W and assume that there is a neutral. I'm not aware of a particular code section that would require the proper label to be installed on the panel but figured I would ask.
Been there, done that. Similar to finding dead fronts that have more breaker knockouts than actual breaker buss spots.......after you bid the jobWell they're going to have to open it to install their circuit. Surprise!, no neutral!
I learned the hard way to open the panel before quoting. There are several brands that have more KO for breakers than spots on the bus. I think they just use the same cover for different size panels to save on mfg and inventory.Been there, done that. Similar to finding dead fronts that have more breaker knockouts than actual breaker buss spots.......after you bid the job
Look at 2020 408.58.Does a 3 phase, 3 wire panelboard require the proper labeling to indicate that it doesn't have a neutral?