I am installing 230 volt - 1 phase equipment in a research lab. The equipment comes from the manufacturer with a cord with a NEMA 14-30P plug (4-wire). However, the neutral is not required, per a note on the equipment drawing that says neutral not connected. The 230 volt distribution in the research lab is 3 phase supplied from a delta secondary transformer, so there is not a neutral available. My question is, can I install NEMA 14-30R receptacles without any connection to the neutral lug on the receptacle without violating the NEC? This receptacle is dedicated to this equipment, i.e. it is not a general purpose receptacle, and could be labeled as "no neutral connected" or something like that. My other option may be to cut the NEMA 14-30P plugs off the equipment and install NEMA 6-30P plugs (3-wire) and NEMA 6-30R receptacles (3-wire). Thanks for your help.