This question could a few different directions. How about giving us an example to work with.Is a 4 wire feeder inherently more safe that a 3 wire in normal conditions? Assume wiring is attached to an OCPD.
If so can you please explain how?
Yes, he needs to make something up. My image was different than yours.This question could a few different directions. How about giving us an example to work with.
If both are done in compliance with the NEC they we can look at each under there own merits.
An example:
A three wire feeder sized correctly for a load is safer than an under sized four wire feeder for the same load.
In the example above the three wire feeder could be three phase three wire load using the EMT as the EGC.
Or a three phase three wire load with a wire type EGC.
So the answer to the question would be. The proper sized three wire feeder using EMT as an EGC running under normal conditions.
The under sized four wire feeder could cause conductor damage with the load operating under normal conditions.
When I say under sized it could be wire size for the feeder based on the load and calculated per NEC.
So make something up and we will run with it.
The only reason it might be less safe is if the ocpd was under sized. The proper application of ocpd is what provides safety, not how many wires.A three wire feeder sized correctly for a load is safer than an under sized four wire feeder for the same load