charlie b said:The four wires would (normally) be Phase A, Phase B, Phase C, and Neutral (grounded). Most water heaters are single phase, and thus would only need two wires. A range might need both single phase 240 volts and single phase 120 volts, and that would require three wires. Generally, only a three phase load would need four wires. Please note that the Equipment Grounding Conductor (green or bare copper) would be in addition to the number of wires described above.
lmchenry said:Thanks Charlie. I should better explain 3-wire wg and 4-wire wg when I am asking such questions.
daddyray said:My house has a 3 wire dryer hookup. Is the third wire a neutral (and thus OK to return the small amt of 120v) but with no ground; or is it a ground (not OK for the 120v, but good for the obvious reasons)?
David
daddyray said:My house has a 3 wire dryer hookup. Is the third wire a nuetral (and thus ok to return the small amt of 120v) but with no ground; or is it a ground (not ok for the 120v, but good for the obvious reasons)?
David
Correct, but under certain conditions as per 250.140. Notice the exception states that ALL the conditions must be met.iwire said:David the NEC has allowed the neutral to be used as the grounding means for electric ranges and dryers.
The frame of the range or dryer is electrically bonded to the neutral at the units connection point.