If i have a 200 amp service on a building 120/240 volts with a 200 amp breaker disconnect on the outside of building must i run 4 wires in to the building?
 

mopowr steve

Senior Member
Location
NW Ohio
Occupation
Electrical contractor
Yes, and don't forget to separate the grounds and neutrals at the panel inside and don't install the bonding screw. Most new panels today are being supplied with the separate grounding bar installed but if it's not there it can be purchased separately.
 
Last edited:

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
It is much easier to install 4 conductor cable than installing a conduit, unless your jurisdiction does not allow cable.
 