40 amp 208v circuit to HWH had a dead short to Ground- Breaker did not trip. Why?

Location
South Carolina
Occupation
Electrician
So plumber was finalizing his end, filled heater with water and went to turn breaker on, upon doing this he said there was an arc where the wires splice to the heater wires. I opened up, one of the legs had been pushed in hard and insulation was nicked by the head of the ground terminal screw. fixed it, turned it on, checked for power, all good. I asked if the breaker had tripped and he said no. it is a standard 2 pole 40, Homeline, 10,000 AIR. What could this be besides bad ground connections, or a faulty breaker?
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Was it really a dead short, like bolted? Or was it a nick in the insulation and the conductor too close to the ground terminal screw? In the latter case, you'll get arcing and possibly even sustained current. But apparently the plumber noticed the problem before there had been a sufficiently large sustained current for sufficiently long to trip the breaker.

Looking at one random 40A breaker trip curve, to guarantee a trip within 60 seconds, the current would have to be about 55A sustained if the breaker was at 40C ambient, but it would have to be 140A at 25C ambient.

Cheers, Wayne
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I would advise taking what others say with a grain of salt be it customers or other tradesmen.
 
Location
South Carolina
Occupation
Electrician
Was it really a dead short, like bolted? Or was it a nick in the insulation and the conductor too close to the ground terminal screw? In the latter case, you'll get arcing and possibly even sustained current. But apparently the plumber noticed the problem before there had been a sufficiently large sustained current for sufficiently long to trip the breaker.

Looking at one random 40A breaker trip curve, to guarantee a trip within 60 seconds, the current would have to be about 55A sustained if the breaker was at 40C ambient, but it would have to be 140A at 25C ambient.

Cheers, Wayne
I guess technically you’re right a dead short would be 0 resistance, and i’d assume that would trip the breaker, i’m also assuming the arc blowout probably stopped the two from touching anymore- assuming that’s the case it probably wouldn’t trip correct?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I agree the fault probably blew itself apart.
But, it is possible for a breaker not to open when our experience says it should. It all depends on how much current was flowing through the breaker and for how long.
You might be amazed at how the resistance of branch circuit wiring can impact breaker opening times. You need the actual utility/supply fault current in order to make the calculation.
 

Seven-Delta-FortyOne

Goin’ Down In Flames........
Location
Humboldt
Occupation
EC and GC
Happens more often than you think.

I was on a service call last week on a bathroom that had intermittent power on several receptacles and one in a medicine cab that nothing would stay plugged in.

I pulled the one in the medicine cabinet out and it completely disintegrated in my hands. The plastic box was melted in the wall, the wiring was fried 6” up in the cavity, and the neutral was only connecting randomly, so the homeowner had trouble getting her curling iron to stay on. 😳😲😳😲

20 amp GFCI breaker never tripped.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Arcs can represent a significant resistance, which can prevent the current flow from being high enough to trip the breaker. That allows the arc to flourish and expand to start a fire, which is one reason AFCI breakers were developed.
 