How come in the NEC exhibit 220.4 in the 2008 handbook ( Rule 220.14 (J))there is a drawing of branch cct loading showing ( 10 outlets on a 15amp cct max, and 13 outlets on a 20 amp cct max ) but then in Mike Holt's understanding NEC 2008 book, fiqure 220-10 pg. 108, the article says that the NEC has no limit on general receptacle and lighting ccts for dwelling units.
I know that everything is suppose to be covered in the 3000 VA rule, but does this mean I can put 40 receptacles on a branch cct? Or am I suppose to just know that I can't. I'm trying to do a calculation and alittle help would be appreicated. Thanks.