We have a couple of service upgrade projects coming up. The buildings are ~40 - 45 years old and the owners want to replace the electric service. They have had the usual problems in getting replacement breakers, adding new ones, etc. and need additional capacity as well.
Replacing the service equipment will be relatively simple. The rub comes in down stream equipment, such as panels, transformers, wiring, etc.
Some of the downstream panels need replacing for the same reasons. Many are flush mounted in corridors, some in "equipment" rooms, etc. We can generally replace the guts and keep the cans.
BUT . . . What about the existing branch wiring/conductors? They are definitely approaching the end of life. Cable manufacturers have quoted 30 - 40 years expected life. Of course, we all know of many sites where the cables are much older and doing just fine.
Replacing the feeders to the down stream panels could be a trick. Getting the old cables out of the existing conduits will be a crap shoot. We had one project where the service cables came out but the conduits were less than 100' and were large enough for the upgraded service. On these projects we have feeders from the service equipment that are 200 - 500 feet long. Just don't see reusing them!
These are community colleges where down time to do work is short. Running new feeders in new conduit is doable but getting in the existing down stream panels would be a trick to say the least!
Then, there is the issue of the wiring for the branch circuits, what about them?
Have any of you run into this? What did you do? The further down stream we go the higher the costs. Where do we stop? We're inclined to stop at down stream panels and leave the branch circuits as the effects of any possible failure would be minor.
What about the 480-120/208V transformers? We're looking at leaving them alone if they "look" ok.
Thanks,
RC
Replacing the service equipment will be relatively simple. The rub comes in down stream equipment, such as panels, transformers, wiring, etc.
Some of the downstream panels need replacing for the same reasons. Many are flush mounted in corridors, some in "equipment" rooms, etc. We can generally replace the guts and keep the cans.
BUT . . . What about the existing branch wiring/conductors? They are definitely approaching the end of life. Cable manufacturers have quoted 30 - 40 years expected life. Of course, we all know of many sites where the cables are much older and doing just fine.
Replacing the feeders to the down stream panels could be a trick. Getting the old cables out of the existing conduits will be a crap shoot. We had one project where the service cables came out but the conduits were less than 100' and were large enough for the upgraded service. On these projects we have feeders from the service equipment that are 200 - 500 feet long. Just don't see reusing them!
These are community colleges where down time to do work is short. Running new feeders in new conduit is doable but getting in the existing down stream panels would be a trick to say the least!
Then, there is the issue of the wiring for the branch circuits, what about them?
Have any of you run into this? What did you do? The further down stream we go the higher the costs. Where do we stop? We're inclined to stop at down stream panels and leave the branch circuits as the effects of any possible failure would be minor.
What about the 480-120/208V transformers? We're looking at leaving them alone if they "look" ok.
Thanks,
RC