I intend to install a 400/320 240v single phase service to my shop. (metal building, concrete slab)
I intend to use a tapped feed to install 2 x 200 amp panels each equipped equipped with a 200 amp OCPD.
I am planning 400 kcmil CU feed from the meter base / 400 amp OCPD to be tapped. (trough)
I plan a #3 CU GEC.
I plan a 2/0 CU conductor (THHN) from the taps off the 400 kcmil feeder from the 400 amp OCPD.
3 inch EMT conduit to be used between the 400 amp OCPD and the trough.
2 inch EMT conduit to be used from the trough to the indoor 200 amp OCPD's.
Both 200 amp panels bonded.
Its been many years and I didnt really have much experience with this type of install.
Does anyone see an issue with my logic?