Chapter 300 wiring method supplies a 2x4 metal box with a receptacle outlet, mounted above a suspended ceiling. A manufacturer's "power supply" box is mounted nearby. The power supply has a flexible cord with a cord cap, and is plugged into the adjacent receptacle outlet. So far, an obvious violation of 400.8(5). Now consider having both the receptacle outlet box and the power supply box, as well as the flexible cord that connects the two, all installed within a NEMA 1 enclosure. It is still above a suspended ceiling. Is it still a violation?
This is what the owner's rep told the contractor to do, and now the owner's rep is saying "oops, bad idea, find another solution." I will post a photo shortly.