Old
400.8
(2) Where run through holes in walls, structural ceilings, suspended ceilings, or floors
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
New/Revision proposal
400.8
(2) Where run through holes in walls, structural ceilings, suspended ceilings, or floors
Exception to (2): As permitted in accordance with the provisions of 410.62(C)(1)
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception to (4): As permitted in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
Exception to (5): As permitted in accordance with the provisions of 410.62(C)(1)
Substantiation: . In their current form, 400.8 and 410.62(C)(1) are in conflict. . This proposal eliminates that conflict without expanding the verbage that could cause the section to become needlessly drawn-out and bloated.
400.8
(2) Where run through holes in walls, structural ceilings, suspended ceilings, or floors
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception to (4): Flexible cord and cable shall be permitted to be attached to building surfaces in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
New/Revision proposal
400.8
(2) Where run through holes in walls, structural ceilings, suspended ceilings, or floors
Exception to (2): As permitted in accordance with the provisions of 410.62(C)(1)
(3) Where run through doorways, windows, or similar openings
(4) Where attached to building surfaces
Exception to (4): As permitted in accordance with the provisions of 368.56(B)
(5) Where concealed by walls, floors, or ceilings or located above suspended or dropped ceilings
Exception to (5): As permitted in accordance with the provisions of 410.62(C)(1)
Substantiation: . In their current form, 400.8 and 410.62(C)(1) are in conflict. . This proposal eliminates that conflict without expanding the verbage that could cause the section to become needlessly drawn-out and bloated.