400 A 3 phase pnl 208/120 volts

Status
Not open for further replies.

Rlmwireman

Member
Location
Evart, MI
Occupation
Electrician
I have a 400 amp disconnect feeding
A 400amp main panel w main.
I gonna run 2 set of 3/0 to 400 amp
Main panel. What size ground in each
Set table 250-122 or 250-66
Thanks
 
250.66 is for GEC's, 250.122 is for EGC's, see the definitions of each in article 100.

Out of curiosity, what year code book are you referencing?

Roger
 
What is upstream of the 400 amp disconnect, and is that disconnect fused? If the answers are "utility-owned transformer" and "no," then the "ground thingy" would be neither a GEC nor an EGC. It would be an SSBJ, and would be sized per 250.102(C).
 