- Washington and Idaho
- Occupation
- Journeyman Electrician
Hi all, i am doing a 400a service 277/480. I have a CT can and a meter can next to it the phases including neutral are all stand offs by insulators. Do i need to bond the neutral to the can? or can i bond the neutral to the first point of disconnect (the Main distribution panel) inside the building? I am hearing i need to do both? As in i would bond the neutral with a 1/0 from the neutral CT to a lay in lug in the can? AND i would bond the neutral and groundbar inside the main panel? So this would mean the neutral is bonded at the can AND the first point of disconnect?
I would assume this is just like a transformer AFTER the main point of disconnect, youd use a supply side bonding jumper from the xo terminal to the ground. Brown h1 orange h2 yellow h3 480 primary, black x1 red x2 blue x3 white x0 and a jumper from x0 to ground. Which can be done in the transformer OR the first point of service. But if you do it in the transformer that makes the 120/208 panel a sub panel and grounds neturals are separated.
main question on the can bonding
Is this correct?
I would assume this is just like a transformer AFTER the main point of disconnect, youd use a supply side bonding jumper from the xo terminal to the ground. Brown h1 orange h2 yellow h3 480 primary, black x1 red x2 blue x3 white x0 and a jumper from x0 to ground. Which can be done in the transformer OR the first point of service. But if you do it in the transformer that makes the 120/208 panel a sub panel and grounds neturals are separated.
main question on the can bonding
Is this correct?