Hello everyone and thank you. I have been a long time forum reader and I'm now currently in the process of Mike Holt's training on the 2023 cycle. I'm sure this type of question has come up before but I had trouble finding it.
That being said, what am I missing?
400 amp 208y/120 three phase main panel service wire size for commercial property. The client moving in is a micro brewery with the only load information being "our family electrician said we maxed out our 200 amp and we need a 400 amp." That's all we have to go with for load calculations. The landlords want us to install the service and they provided a 400 amp main panel. The wire will be aluminum and ran in 2 runs parallel. Each run will be in PVC underground from the utilities disconnect to the panel.
Assuming that most of the loads won't be 3 phase, I'm calculating the neutral as a current carrying conductor. Wire will be modern wire and either of the RHW-2 or THWN-2 multi-rated jacketed wire family. Lugs are 75C.
If I use the 75C column for the aluminum wire, then derate to 80% { 310.15 (c)(1) 4 current carrying conductors} I have to use a 350kcmil wire to get up to exactly 400 amps. The lugs on the meter can and disconnect provided by the city only go up to (2) 250kcmil. I know it's a 320 amp continuous and 400 amp peak meter. Anything above that and the city puts you on demand. If I use the 90C column to derate my wire, I can get by with a 300kcmil but that still doesn't explain why my factory lugs are only good for up to (2) 250kcmil. And by going to the 90C column for my wire wouldn't I violate 110.14 (c)?
If the meter can is only good for 320 amps, is that what I size to? If I do then (2) 250kcmil at 75C gets me to 328 amps which is over 320 amp but a long ways away from 400. At 90C (2) 250kcmil only gets me to 368 amps. I feel like having 400 amp fuses (city's fused disconnect), and a 400 amp main, I should be a lot closer to that 400 amp mark and if the meter fails, that's the city's problem to replace. I know you can round up breaker size to the next size breaker { 240.4 (b) } but I have no way of knowing the trip settings on the used main breaker the client provided.
I had felt confident in my in my 350kcmil calculations until I noticed the factory installed lugs weren't big enough. Then I started to second guess myself and now I feel like I'm missing something drastic and possibly over-sizing my wire but I want to do it right. If I have missed something please quote the reference number so that I may read it myself.
Again thank you.
That being said, what am I missing?
400 amp 208y/120 three phase main panel service wire size for commercial property. The client moving in is a micro brewery with the only load information being "our family electrician said we maxed out our 200 amp and we need a 400 amp." That's all we have to go with for load calculations. The landlords want us to install the service and they provided a 400 amp main panel. The wire will be aluminum and ran in 2 runs parallel. Each run will be in PVC underground from the utilities disconnect to the panel.
Assuming that most of the loads won't be 3 phase, I'm calculating the neutral as a current carrying conductor. Wire will be modern wire and either of the RHW-2 or THWN-2 multi-rated jacketed wire family. Lugs are 75C.
If I use the 75C column for the aluminum wire, then derate to 80% { 310.15 (c)(1) 4 current carrying conductors} I have to use a 350kcmil wire to get up to exactly 400 amps. The lugs on the meter can and disconnect provided by the city only go up to (2) 250kcmil. I know it's a 320 amp continuous and 400 amp peak meter. Anything above that and the city puts you on demand. If I use the 90C column to derate my wire, I can get by with a 300kcmil but that still doesn't explain why my factory lugs are only good for up to (2) 250kcmil. And by going to the 90C column for my wire wouldn't I violate 110.14 (c)?
If the meter can is only good for 320 amps, is that what I size to? If I do then (2) 250kcmil at 75C gets me to 328 amps which is over 320 amp but a long ways away from 400. At 90C (2) 250kcmil only gets me to 368 amps. I feel like having 400 amp fuses (city's fused disconnect), and a 400 amp main, I should be a lot closer to that 400 amp mark and if the meter fails, that's the city's problem to replace. I know you can round up breaker size to the next size breaker { 240.4 (b) } but I have no way of knowing the trip settings on the used main breaker the client provided.
I had felt confident in my in my 350kcmil calculations until I noticed the factory installed lugs weren't big enough. Then I started to second guess myself and now I feel like I'm missing something drastic and possibly over-sizing my wire but I want to do it right. If I have missed something please quote the reference number so that I may read it myself.
Again thank you.